Series 7000/7100 and 7200/7300 Data Presentation Differences

For the purposes of this article, we will refer to the 7200/7300 family of meters as the "virtual element" (VE) style meters.

Virtual vs. Non-Virtual Meter Elements: What’s the Deal?​

If you’ve ever tried to integrate a power meter and found yourself knee-deep in Modbus IDs and register maps, you’re not alone. One of the most common points of confusion? The difference between “virtual” and “non-virtual” meter elements and how their data point mapping differs. This article will help break down those differences.

Series 7000/7100 Standard Elements​

These are your classic, physical meter elements. Here’s how they work:
  • Element Count: Depending on the model, you’ll get anywhere from 1 to 16 elements. Each element has up to 3 CT landings for monitoring an energy load or source.
  • Quick Math Trick: Take the last two digits of the meter's part number (say, 71d12), divide by 3 to calculate your total number of elements.
  • Modbus RTU IDs: The base Modbus ID# you set in the meter corresponds to Element A. Each additional element gets the next ID up (B = base+1, C = base+2, etc.).
  • Modbus TCP: Things are simpler here—ID#1 always starts with Element A, no matter what.

Virtual Element Meters (7200/7300 Series)​

Here’s what makes them unique:
  • Element Count: Up to 24 virtual elements can be created with flexible use of each individual CT input on the meter, allowing for combining up to three CTs to one element.
  • Modbus-Only: These meters are designed strictly for Modbus RTU or TCP.
  • Single Modbus ID: Unlike the standard meters, all virtual element data lives under one Modbus ID#.
  • Simplified Data Points: Each virtual element only gives you the essentials—Energy, Power, and Power Factor. That’s it. You’ll find these in the register map under the “virtual element” sections.
  • Voltage References: The meter circuit board and terminals will have two sets of voltage reference landings, but only the first set is usable when you’re working with a virtual element meter.

Summarizing The Differences​


FeatureSeries 7000/7100Series 7200/7300
Modbus ID#One per element (A, B, C...)One for all virtual elements
Data PointsAdvanced data set of per element and per phase measurementsEnergy, Power, Power Factor only
ProtocolsModbus RTU and TCP
BACnet MS/TP and IP
Modbus RTU
Modbus TCP
Voltage ReferencesTwo services with three phases or lessOne service
 