How many devices or datapoints can I log with my EMH?

This article is to cover how many nodes, devices, and datapoints can be associated with a single EMH. This article is intended for the A7810, A8810, A8812 and A8814 model Leviton Energy Monitoring Hub dataloggers. For the newer models, please review this communities article for more details.

Definitions:
Node:A physical device on the RS485 daisy chain
Device:A physical or virtual instance where device datapoints are made available for capture
Datapoint:Any measurement or status parameter available to be read from a device

System Recommended or Hard Maximums:
When designing a system, the general recommendations we have for the dataloggers listed above are:
  • Up to 100 devices on the Device List from any of the following sources:
    • RS485 Modbus
    • Modbus TCP
    • BACnet IP
  • Up to 32 total nodes on any physical RS485 daisy chain
  • 4000 total datapoints across all devices
Additional factors that should be considered which may adjust what the recommendations would be are:
  • Logging rate
  • Acceptable latency for the last device's data to be captured
  • Baud rate
  • Device response times
  • # of separate Modbus register block(s) needed
  • Frequency of communication errors
  • Months/Years of offline data storage capacity
  • # of configured logged data upload channels
For deployments with multiple EMH dataloggers, it is best to try and evenly balance the total number of datapoints associated with each system.


Common product part numbers and typical system load:
ModelNodesDevicesDatapoints
EMH A8810100
EMH A88121146
Flex I/O A83321146
High Density Pulse Module A89111146
ModHopper R91201110
EMH A78101120
Series 40001137
Series 41001172
Series 60001164
Series 7000/7100, 48 input version116992 (62/device)
Series 7000/7100, 24 input version18496 (62/device)
Series 7000/7100, 12 input version14248 (62/device)
Series 7000/7100, 3 input version1162
Series 7200/73001172
Series 800011313
 
Last edited: