Best practice when Using a Low voltage DRC room controls with generator power.

Kevin Bannon

New member
Low voltage room control with emergency power application. 1 x DRC00-0L0 room control communicating with 2 x DRDDP-A40 in an application. The DRC00-0L0 is connected to emergency power source through the EM panel. When the generator is cycle tested the dimmed phase loads do not return to the most recent pre-set levels. Is there a method to have the phase loads return to the preset level after emergency power is cycled.
 
The power-restore feature will need to be enabled for the DRDDP-A40. I thought this was enabled by default. I will go check and get this moved into the next firmware release.
 