I need to power the switch for a T2799 GFCI combination switch and receptacle. The power is connected and the GFCI indicater light is on and the switch leads are connected to the two black leads that are preconnected to the switch But I have to provide power to the switch. Where do I connect the jumper? Thanks

  • Leviton T7299
    Scout

    Paul,

     

    The switch leads should only connect to the load you wish to control. Make sure the load has a proper ground and neutral connection, as the neutral wire will be passing the power to the load.  The LOAD terminals should only be used if you're connecting other receptacles downstream which you'd like to provide GFCI protection for.